I have an AHJ who is telling me that I need to rotate my design area length
90 degrees to account for there not being enough sprinklers per line on the
branches.  This would give me a design area that is perpendicular rather
then parallel per 14.4.4.1.11.  Section 14.4.4.1.1.3 states, “In systems
having branch lines with an insufficient number of sprinklers to fulfill the
1.2 requirement, the design area shall be extended to include sprinklers on
adjacent branch lines supplied by the same cross main.”  I was taught, and
therefore I have always understood this to mean that in a situation where
there are not enough sprinklers per line you include additional sprinklers
up to the point that your design are is fulfilled, i.e. add sprinklers until
I reach 1500 sf, not until I have created a perpendicular area of 46 + ft.
Is this the same understanding that everyone else has?