Yep.  

And this is not an isolated story. In my jurisdiction we experienced a
roof fire as a result of a torch operation. FD arrived hooked up to the
first standpipe, no water.  I disconnected the line and ran down the
hallway to the next standpipe which was operational. Ironically there
was an inspection decal emblazoned with the contractors name, phone
number, license number and current inspection. The decal, nor any report
noted any deficiency. It was discovered that the standpipe had been
taken out of service to facilitate a piping change as part of a
construction project but was never reconnected, something that should
have been done immediately. 

The fire code order that followed required the witnessed reinspection of
the entire standpipe system where numerous violations such as leaking
valves were discovered. All of this by a licensed fire suppression
contractor. 

We lucked out in that it was a minor fire and an alternate source of
water was available, but what if it wasn't ?.

John Drucker
Fire Protection Subcode Official (AHJ)
New Jersey

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Matt
Willis
Sent: Tuesday, August 21, 2007 8:16 AM
To: [email protected]
Subject: More victims still...

http://cms.firehouse.com/content/article/article.jsp?sectionId=39&id=560
32
 
 
 
Matthew J. Willis
Living Water Fire Protection, LLC.
1160 McKenzie Rd.
PO Box 877
Cantonment, FL. 32533
850-937-1850 Voice
850-937-1852 Facsimile
[EMAIL PROTECTED]
 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to