If you're using it as your check valve then yes. If you have another
check in the riser (AV) then no. That's by 7.1.1.2 as mentioned by the
others (I hope some of you got that and I hope that more got it now
that I pointed it out). Enforcement around here is spotty. If it's
residential there doesn't seem to be much concern about it in these
parts. By USC rules puttint anything but the test gauge hose adapters
on any of those test cocks would be considered altering the device and
abbrogating its listing. You have to watch out for backflow nazis.

On 8/23/07, å... .... <[EMAIL PROTECTED]> wrote:
> got a request by reviewing authority to put a
>
>     pressure gage on the supply side of a BFP.
>     We have one on our slick riser, but is one
>     required on the supply side?  Sounds like
>     a good idea.  But don´t most BFP´s have
>     mounts for installing and removing gauges?
>
> The BFP is our system check valve.
>
> Scot Deal