Pete, 2002 NFPA-13;
11.2.1.3, Occupancies or "portions of occupancies, shall be classified....." 5.3.1, Ordinary Hazard Group 1 "do not exceed 8 feet...." Hope that helps John Drucker Fire Protection Subcode Official New Jersey -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Larrimer, Peter A Sent: Monday, August 27, 2007 10:44 AM To: [email protected] Subject: Incidental Storage List members. If a room, say 20 ft. by 20 ft., in an overall light hazard occupancy is used for storage of combustible materials (i.e. ordinary hazard) stacked say 8 feet high, does NFPA 13 require that space to have OH density and spacing criteria met? I remember a discussion on this sometime in the past but I can't find anything definitive in NFPA 13 that wouldn't require you to apply the OH rules. Thanks Pete _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)