The baffles are 8 feet wide and are about 80 feet long. I haven't completely grasped how this structure is going to look since the section views aren't consistent with either the front or plan views.

At 04:20 PM 8/27/2007, you wrote:
If the baffles are 8 ft. long how wide are they?

The real question should be are only three levels of sprinklers adequate
for light hazard?

Ron Fletcher
Aero Automatic Sprinkler
Phoenix, AZ

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams - work
Sent: Monday, August 27, 2007 9:10 AM
To: [email protected]
Subject: Obstruction issue

I am working on a project with a rather complex ceiling system. The roof
is steel deck, below the steel are some T shaped baffles and below that
is a fabric ceiling which is stepped with vertical openings. (This is
for a church. You sometimes find similar looking ceilings in theaters,
sans fabric). My proposal is to install sprinklers at the deck, under
the baffles and beneath the fabric. I have two questions:

First, the T shaped baffles are 8 feet wide with a member perpendicular
near the mid point. one side is 4'-2" and the other 3'-10" . three feet
away, there a three foot wide baffle and three feet from that, another
T. My instinct tells me to put a sprinkler on both sides of the vertical
member. The engineer is looking at everything closely, because he
basically showed sprinkler below the fabric and that is it (and is now
in the hot seat). Any good justification I can use for adding the
sprinkler (assuming it is questioned)?

Secondly, NFPA 13 (2002) section 11.2.3.1.8(6) says that sprinklers
below obstructions do not need to be included in the hydraulic
calculations. I am having a hard time accepting this as well because I'm
not sure the potential fire demand will only include sprinklers at the
deck. Actually, sprinklers at the deck may be so obstructed that very
little will effectively get to the fire area. I would think it be more
than likely a combination of sprinklers above and below.
Any thoughts?

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
860-535-2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
860-535-2080
www.fpdc.com
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to