You are providing confusing information.  Normally you would not include the
sprinkler demand with the deluge demand.  It looks like you have two demand
conditions - deluge + hose = 1800 gpm and sprinkler + hose = 1000 gpm.  Why
do you use 2500 gpm for your demand?

Bill Brooks

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] Behalf Of Reza
Esmaeili
Sent: Wednesday, September 05, 2007 12:43 PM
To: [email protected]
Subject: RE: Fire Pump Selection - Another Question


According to NFPA answer, you were right Richard, howeever NFPA answer was
short for item 3.
  What I want to ask is simulating a real project like below:
  Imagine in a factory I want to select fire pump for my below demand:
  1- Total demand of deluge system: 1500 GPM
  2- Total demand of wet pipe sprinkler system: 700 GPM 
  3- Total demand of hose streams: 300 GPM.
   
  Total water demand: 2500 Gpm, Total pressure: 100 psi
  For this project as my source of power is reliable, I want select TWO
parallel electric pumps with below specifications:
   
  Scenario 1: Two pumps( First: 1250Gpm ,100 Psi - Second: 1250 Gpm ,100Psi
)
  Scenario 2: Two pumps( First: 1500Gpm ,100 Psi - Second: 1000Gpm ,100Psi )
  Scenario 3: Two pumps( First: 1500Gpm ,100 Psi - Second: 1500Gpm ,100Psi )
   
  As my deluge demand is 1500 GPM, so which scenario is the best for my
project?
  Note that I want to select one of the above scenarios and don't have any
other options.
  Would you also please analyze each item.
  Thanks,
  Reza

       
---------------------------------
Be a better Heartthrob. Get better relationship answers from someone who
knows.
Yahoo! Answers - Check it out. 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to