Steve,
I've done several of these. What I do is to find out what the
intended uses are from the owner or architect and design to that.,
with a note if necessary. For the most part, the intended use has
fallen into LH criteria, but you never know. It's difficult to
predict what brilliant idea someone will come up with in the future,
so find out what their intentions are and design for that and CYA.
At 12:32 AM 9/8/2007, you wrote:
What is the consensus for classifying the hazard level of multi-purpose
areas in churches? I seem to remember this being discussed before but
cannot find anything in the archives. I am looking at a 17,000 sqft church
with a large central sanctuary/gymnasium/multi-use area. I would think that
light hazard protection would be inadequate because of the probable use of
the space for bazaars, shows, exhibits, bake sales, etc. but I'm wondering
what the best approach is.
Have a good weekend and thanks in advance for any help.
Steve Kowkabany, P.E.
Fire Protection Engineer
Neptune Fire Protection Engineering LLC
216 Seagate Avenue Unit B
Neptune Beach, FL 32266
904-652-4200 Phone
904-212-0868 Fax
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)