10-4
thanks 

 
 
 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Mike Brown
(TECH- GVL)
Sent: Wednesday, September 19, 2007 2:06 PM
To: [email protected]
Subject: RE: Mixing Heads

You may want to note that you cannot put a sprinkler in the listed spray
pattern of another sprinkler.  This sometimes causes problems where you may
want to put a standard spray sprinkler in an area with an extended coverage
sidewall sprinkler.
Mike Brown

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ron Greenman
Sent: Wednesday, September 19, 2007 1:50 PM
To: [email protected]
Subject: Re: Mixing Heads

Correct.

On 9/18/07, Brian Harris <[EMAIL PROTECTED]> wrote:
> Somebody please refresh my memory, it's o.k. to have both Extended
coverage
> & Standard coverage heads in the same area correct? Isn't different
temp
> ratings or RTI's that you cant mix?
>
> Thanks
>
>
>
>
>
>
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email
to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>


--
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to