On another subject, excellent AFSA bulletin on grounding and bonding sprinkler piping. This is an area that even electrical contractors have trouble with. As the article notes its imperative that bonding and grounding be distinguished. The difference is significant. While using sprinkler piping as a grounding electrode is prohibited, bonding metallic sprinkler piping is mandatory pursuant to the National Electrical Code.
Unfortunately I still find bonding connections being removed by misinformed sprinkler personnel. This action not only is a violation of the electrical contractors act and the NEC but actually increases the risk of electrocution to sprinkler fitters and inspection personnel. Without the bonding connection to the buildings electrical service it is entirely possible, especially in wooden structures, that sprinkler piping can become energized. It could be as simple as an open 277 volt lighting circuit laying across a section of 1" black steel. The mechanic who makes the connection to ground or another bonded object completes the circuit risking injury or death. So for the sake of sprinkler personnel make sure all metallic sprinkler piping is properly bonded by the electrical contractor. As a matter of fact the next time you cant find the bonding connection ask why and insist that it be made for your own safety. Great Job AFSA. Sincerely, John Drucker Fire Protection Subcode Official Licensed Electrical Contractor New Jersey _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)