Remember to consider 20 psig at the sprinkler if the spacing perpendicular to the slope is > 8 ft. This applies to SSP & SSU. 2007 nfpa Table 8.6.2.2.1(a).
Which brings up a question: besides the listed "attic sprinkler" and SSP´s and SSU´s... what OTHER sprinklers are approved for use in sloped attics? Would residential sprinklers listed for beamed ceilings with pitches up to 8 in 12 be approved for attics? scot deal excelsior fire engineering _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)