Yes, if over 750 gallons.  Under 750 you still get the choice of the quick
opening device with time not mattering and under 500 time doesn't matter -
no manifold no program.  The time could be as low as 40 sec. depending on
the hazard.  See 7.2.3.1 in the '07. Table 7.2.3.6.1 goes with it.  