Peter,
As far as calculating modifications to an existing system, assuming that you
are talking about relocated sprinklers or sprinklers added off of existing
lines, there is no implicit direction to calculate or not to calculate.
This is a situation that would require a judgment call.  If it is not
calculated certain information would need to be known, such as original
sprinkler spacing, pressure and flow requirements, hazard, etc...  If, say
for instance, a few sprinklers are being added because a larger room has
been divided into smaller rooms, then calculations may not be necessary so
long as the new sprinklers are not creating a greater demand then the
original sprinklers.  For instance, the original density was .2 over 130 sf
per head and the new sprinklers are being installed in areas that will only
require a density of .10 over 168 sf per head.  The net change in demand is
actually less then the original and calculations shouldn't be required.
But, on the other hand, if the area in question creates a greater demand
because more sprinklers are being introduced into the area that originally
had 10 sprinklers at .2 and now ends up with fourteen sprinklers,
calculations would be warranted.
Anyway, I don't know if this is explained as well as it could be, but I hope
it helps.  The bottom line is what is the net overall change to the area
affected?  Based on this information a determination can be made as to
wheatear or not you will need calculations.

Just my opinion,
Bob Knight

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Larrimer,
Peter A
Sent: Thursday, October 18, 2007 8:10 AM
To: [email protected]
Subject: Minimum Number of Sprinklers for Recalc?

Is there anywhere in 13 where it permits you to perform a minor
modification to a hydraulically calculated system and not have to
re-calculate the changes?  I can't find it if there is such a
permission.  

Thanks

Peter Larimer
VA


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

No virus found in this incoming message.
Checked by AVG Free Edition. 
Version: 7.5.488 / Virus Database: 269.15.0/1077 - Release Date: 10/18/2007
9:54 AM
 

No virus found in this outgoing message.
Checked by AVG Free Edition. 
Version: 7.5.488 / Virus Database: 269.15.0/1077 - Release Date: 10/18/2007
9:54 AM
 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to