If you have to chose between the two, use the spacing as if the wall
were solid, and ask to install a baffle from the top of the wall down
2'-0" to stop the cold solder. If visibility is an issue use a clear
element for the baffle such as glass or poly carbonate sheets.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message ----- From: "Bobby Gillett"
<[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Monday, October 22, 2007 1:38 PM
Subject: RE: Vertical mesh wall
Thanks for your reply. I pretty much need to go one way or the other,
due
to the spacing from walls to mesh wall on each side and the spacing of
the
sprinkler, I can't accommodate both. I'm either going to cold solder
or be
over spaced. That's why I was looking/hoping for a limitation/definition
that would draw the line.
Bobby Gillett
Project Manager
[EMAIL PROTECTED]
(731)-424-0130
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bob Knight
Sent: Monday, October 22, 2007 2:21 PM
To: [email protected]
Subject: RE: Vertical mesh wall
Bobby,
In my opinion, which isn't always as humble as it needs to be, since
this is
not LH, the sprinklers will need to maintain their minimum separation and
the sprinklers will need to be spaced treating this as an obstruction to
discharge (i.e. half the distance). The mesh will allow water
through, but
it will also impede proper distribution. Because of this I believe
that the
minimum distance between sprinklers will need to be maintained to prevent
cold soldering and since distribution will be affected, half the distance
will need to be maintained.
Just my opinion if I were the layout guy,
Bob Knight
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bobby
Gillett
Sent: Monday, October 22, 2007 1:03 PM
To: [email protected]
Subject: RE: Vertical mesh wall
This is Class IV comm and we have EC sprinklers (storage room in
Grocery/Shopping store). Wall of mesh keeps people out of a certain
area in
the back store room.
Bobby Gillett
Project Manager
[EMAIL PROTECTED]
(731)-424-0130
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bob Knight
Sent: Monday, October 22, 2007 2:00 PM
To: [email protected]
Subject: RE: Vertical mesh wall
Since this is in the vertical plane wouldn't this fall into the "MESH"
criteria in 8.6.5.2.2 for LH only occupancies?
Bob Knight
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of George
Church
Sent: Monday, October 22, 2007 12:47 PM
To: [email protected]
Subject: RE: Vertical mesh wall
This may or may not help, but >70% unobstructed is what we've seen
applied
by a reputable independent fire tester/underwriter on similar items.
glc
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bobby
Gillett
Sent: Monday, October 22, 2007 2:39 PM
To: [email protected]
Subject: Vertical mesh wall
We have a 2x4 metal stud wall on 16" centers with ½"x½" hardware cloth
on it
to deck. Is this considered a wall? I can't seem to find the size
limitations to the openings.
Thanks,
Bobby Gillett
Project Manager
[EMAIL PROTECTED]
(731)-424-0130
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
No virus found in this incoming message.
Checked by AVG Free Edition.
Version: 7.5.488 / Virus Database: 269.15.5/1085 - Release Date:
10/22/2007
10:35 AM
No virus found in this outgoing message.
Checked by AVG Free Edition.
Version: 7.5.488 / Virus Database: 269.15.5/1085 - Release Date:
10/22/2007
10:35 AM
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
No virus found in this incoming message.
Checked by AVG Free Edition.
Version: 7.5.488 / Virus Database: 269.15.5/1085 - Release Date:
10/22/2007
10:35 AM
No virus found in this outgoing message.
Checked by AVG Free Edition.
Version: 7.5.488 / Virus Database: 269.15.5/1085 - Release Date:
10/22/2007
10:35 AM
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)