Does anyone have any experience with rack storage of polyester fabric on
paper rolls?

 

-          double row racks,

-          solid shelving,

-          3 levels of storage (2 solid shelves) not greater than 60" apart
vertical,

-          3" transverse flues at the rack uprights,

-          No longitudinal flues,

-          max storage height is 14 ft., and

-          T.O.S. is 16 ft.

 

I know solid shelves are ugly, but as we all know, not much guidance is
given in NFPA 13 -2002.

 

I came up with one level on in-racks + .285 / 2000.  Looking at the fire
test data, it recommends providing additional protection and I was thinking
of tightening up the in-rack spacing and providing face sprinklers.

 

Any assistance or advice is appreciated.

 

 

 

Regards,

 

Sean W. Conlin, A.Sc.T.

DEMAND SPRINKLER DESIGN INC. 

E:   <mailto:[EMAIL PROTECTED]> [EMAIL PROTECTED]

 

 

 

 

 