Chris,

The simple reason is that the test for K25s was run at 50 psi because the manufacturer wanted a success and there was no previous data. The test could be re-run at a lower pressure anytime somebody wants to to risk the money it would cost.

K25 applications are based on individual tests because there performance isn't equal to K14s on a flow-to-flow basis. K17s are close enough to K14s to allow extrapolations from K14 tests on a flow-to-flow basis in most cases.

Anytime you treat NFPA 13 as a scientific, consistent engineering document, you're asking for trouble! It's a large collection of loosely connected fire protection rules that range from well-supported to unsupported, depending on when and under what circumstances they were adopted. That doesn't make it a bad standard to follow, but it does make it impossible to read between the lines without risking faulty conclusions on occasion.

The best examples are the curves for class I-IV commodities that are read down to the third decimal place. The vast majority of the tests behind the curves (all of which were done more than 35 years ago) were done with class II commodities. The class III curve was based on two tests of greeting cards in boxes and drawing a "curve" through these two points parallel to the class II curve (with no safety factor applied). The class IV curve was done the same way (two tests of a mixture of plastic tape, sandpaper, etc), except that both of the tests would be considered failures if repeated today. There were no class I tests. A curve parallel to the Class II curve was drawn arbitrarily. So why haven't we been burning down warehouses? The two biggest reasons are that the test were run with K5.6 sprinklers and economics have dictated K8 sprinklers almost from the beginning, and the tests had to be controlled by sprinklers for 30 minutes in order to be a success when Fire Departments arrive more quickly in most cases. (By the way, those that believe that the reason real world sprinkler systems do better is the high start pressure and declining density aren't on firm ground, either. In testing, this has been proven to be wrong several times.)

Those designers who play the game of sliding up the curve to sneak by with 130 sq.ft. spacing and/or K5.6 sprinklers to save a few pennies do so at the cost of fire protection that is on the ragged edge, even though 13 can be interpreted to say that any point on the curve with any sprinkler and any spacing will provide the same protection.


Joe

Chris Cahill wrote:
Anyone have a theory why uncartoned unexpanded plastics doesn't follow the
pressure patterns of everything else. In all other cases outside this the
smaller the orifice the larger the pressure.

For example 25' storage ESFR 25 - 50 psi, ESFR 14 - 50 psi, ESFR 17 - 35
psi.   Slight changes as the storage gets higher but still really not
consistent with the general pattern.
Also flies in the face of the general rule of the larger the orifice the
better the fire control.  Not really important just something I noticed this
morning and made me curious.
Chris Cahill, P.E.

Fire Protection Engineer

Sentry Fire Protection, Inc.

763-658-4483

763-658-4921 fax

Email: [EMAIL PROTECTED]

Mail: P.O. Box 69

        Waverly, MN 55390

Location: 4439 Hwy 12 SW

              Waverly, MN 55390

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to