I wonder if Section 1504.4 of the 2006 International Fire Code would address 
your question.

"Spray booths and spray rooms shall be protected by an approved automatic 
fire-extinguishing system complying with Chapter 9. Protection shall also 
extend to exhaust plenums, exhaust ducts and both sides of dry filters where 
such filters are used."

Craig Rauch, Certified Fire Safety Inspector
Washington Township Fire Department

-----Original Message-----
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Greg McGahan
Sent: Wednesday, December 12, 2007 11:58 AM
To: [email protected]
Subject: RE: paint spray booths

OK, I believe you no problem, but where does it say that?

Also, are there any of these high dollar booths that do not pick up paint
particles behind the filters? I would assume the new ones either all do or
all do not.
Greg

Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of art
Sent: Wednesday, December 12, 2007 10:34 AM
To: [email protected]
Subject: RE: paint spray booths

Exhaust ducts that can pick up paint spray materials are all required to
have sprinklers, in plenums behind the filters up to the roof or wall to
outside.

Art

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Greg McGahan
Sent: Wednesday, December 12, 2007 11:19 AM
To: [email protected]
Subject: paint spray booths

Does 13 or 33 REQUIRE sprinklers in the ducts of a paint spray booth or
only in the manifold where 2 ducts join together. There are references
to when sprinklers are provided but no reference to when they are
required that I can find.

Help?

Greg



Living Water Fire Protection, LLC

1160 McKenzie Road

Cantonment, FL 32533

850-937-1850

Fax: 850-937-1852



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to