Forumites,
A question has arisen here on the correct application of a particular
paragraph of NFPA-13, 2007 ed.
"Section 11.2.3.1.4 (3) Unless the requirements of 11.2.3.1.4(4) are met
for buildings having
unsprinklered combustible concealed spaces, as described in 8.15.1.2 and
8.15.6, the minimum
area of sprinkler operation for that portion of the building shall be
3000 ft2 (279 m2). The design
area of 3000 ft2 shall be applied only to the sprinkler system or
portions of the sprinkler system
that are adjacent to the qualifying combustible concealed space."
Here's the two issues we're discussing:
1) If the space in question must does not meet any of the conditions in
11.2.3.1.4(4) and does meet
the descriptions in 8.15.1.2 and 8.15.6, and the area of sprinkler
operation is increased to 3,000
square feet, is it acceptable to reduce the density for the area to the
value shown in Figure 11.2.3.1.1?
For example, if we're covering light hazard occupancy, and are forced to
the 3,000 square foot remote
area, is it acceptable to use a density of 0.07 gpm per square foot?
2) If the area of operation is increased to 3,000 square feet by this
section, can the reduction for use of
quick response sprinklers in areas with ceilings less than 20'-0" in
height as noted in 11.2.3.2.3.1 be
applied?
The reason for asking #1 is that this section makes mention of an
increase in the operating area without
noting "without revising the density" as is found in the sections which
establish the increase for dry
systems and sloped ceilings greater than 2:12. So, because it's not
there does that mean the density
can be revised?
The reason for asking #2 is that there's no clear guidance as to whether
the minimum remote area can be
reduced using QR's and low ceilings.
Any help, greatly appreciated.
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> e-mail
www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website