Russ, In addition to the comments offered by forum members consider a 30 degree down elbow when using 5" LDH/Storz on FDC's. The stress on the hose is considerable straight out. Most if not all fire apparatus are now equipped with down elbows for LDH (Large Diameter Hose - 5" and Larger).
http://www.kochek.com/PROD3.htm http://www.harrinc.com/catalogdb/catalog_results.php John Drucker Fire Protection Subcode Official (AHJ) New Jersey -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Russell Sent: Friday, December 21, 2007 10:39 AM To: AFSA Subject: Storz Connections I've a project which requires Storz FDCs and I know nothing about these types. All I know is the end the fire department connects to is to be 5". They come in varying pipe sizes on the side that connects to the sprinkler system. Is there anything special on determining the size of this pipe? Thanks, Ron Internal Virus Database is out-of-date. Checked by AVG Free Edition. Version: 7.5.467 / Virus Database: 269.8.13/843 - Release Date: 6/10/2007 1:39 PM _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)