Ya lost me on it doesn't matter if there are 8" lintels. You must be
talking about the '07. The way I read that is the 8" lintel defines the
room not whether you calc the head (or 2) outside the room.
If there is a lintel and isn't a self closing door you add heads. If there
isn't a door and isn't a lintel it's part of the primary room and you
continue to find a (all) door(s) or lintel(s) to stop defining the largest
room. Then you add or don't add heads on the other side depending on the
closer. Then there is a 36" exception to really mess this up.
I will agree it is a poorly written section.
Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
763-658-4483
763-658-4921 fax
Email: [EMAIL PROTECTED]
Mail: P.O. Box 69
Waverly, MN 55390
Location: 4439 Hwy 12 SW
Waverly, MN 55390
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Jeff Hewitt
Sent: Friday, December 21, 2007 9:34 AM
To: [email protected]
Subject: Re: Room Design
Bill,
Are they propped open with a fusible link??? You know, the 3-hr. wooden or
rubber wedge fusible link??
Seriously, if these are light hazard spaces, the doors being open may not
matter if you have minimum 8-in. lintels.
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO 63301
636-946-0011
636-946-5172 (FAX)
This e-mail and any attachments are CONFIDENTIAL and may be protected by one
or more legal privileges. It is intended solely for the use of the
addressee identified above. If you are not the intended recipient, any use,
disclosure, copying or distribution of this e-mail is unauthorized. If you
received this e-mail in error, please notify the sender immediately at the
above captioned address.
----- Original Message -----
From: <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Friday, December 21, 2007 9:13 AM
Subject: Room Design
> When you are performing an inspection of a system calculated using the
> room design approach, how do you handle all of the doors that are
> propped open?
>
> Or, how do you calculate these systems? Do you always go with the extra
> two sprinklers and assume the doors will be held open?
>
> Bill Brooks
>
> William N. Brooks, P.E.
> Brooks Fire Protection Engineering Inc.
> 372 Wilett Drive
> Severna Park, MD 21146
> 410-544-3620 Phone
> 410-544-3032 FAX
> 412-400-6528 Cell
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)