the FDC needs t be fed from a hydrant on the source side of the dcda in
order to work properly.

Garth

----- Original Message ----- 
From: "Charles Thurston" <[EMAIL PROTECTED]>
To: "Greg McGahan" <[email protected]>
Sent: Thursday, January 10, 2008 2:43 PM
Subject: Re[2]: fdc loop


> Hello Greg,
>
> Looks like a check valve is needed in the leg of the tee that feeds
> the standpipe and sprinkler. The FDC needs to be connected to that
> legs also before that check valve. Otherwise it is a useless loop as
> you suspect.
>
> This is how I see your drawing, I condensed it a little to stop line
> wrap.
>
>  Hydrants are "O" and fdc is "X"
>                    STANDPIPE
>
>                    I
>                    I
>  "O"        O"     I
>   I---------I------I-------"X"----dcda-----SOURCE
>
>
>   "I" belive it should look like this:
>
>  Hydrants are "O" and fdc is "X"
>  ^ is a check valve
>
>                    STANDPIPE
>
>                    I
>                    I
>                   "X" fdc
>                    I
>  "O"        O"    "^" check valve
>   I---------I------I--------------dcda-----SOURCE
>
>
>
>
>
>
> Thursday, January 10, 2008, 1:51:48 PM, you wrote:
>
> > My picture did not work, sorry.
>
> > Deal is this: Source to backflow with FDC, 6" continues to tee that
feeds
> > standpipe and sprinkler, from the tee 6" continues to 2 fire hydrants.
>
> > When FD connects to hydrant they will connect back to fdc with the
sprinkler
> > main in between the 2. Will this create a useless loop or will it work?
> > Thanks,
> > Greg
>
> > Living Water Fire Protection, LLC
> > 1160 McKenzie Road
> > Cantonment, FL 32533
> > 850-937-1850
> > Fax: 850-937-1852
>
>
> > -----Original Message-----
> > From: [EMAIL PROTECTED]
> > [mailto:[EMAIL PROTECTED] On Behalf Of Greg
McGahan
> > Sent: Thursday, January 10, 2008 9:09 AM
> > To: [email protected]
> > Subject: fdc loop
>
> > We have a situation as follows:
>
> >
>
> > Hydrants are "O" and fdc is "X"
>
> >
>
> >
>
> >                                                STANDPIPE
>
> >                                                              I
>
> >                                                              I
>
> > "O"                                         "O"      I
>
> >
> >
I----------------------------I------I-------------------------"X"-dcda------
> > ---SOURCE
>
> >
>
> > Question: Will this work or does it create a loop that will prevent the
> > standpipe from receiving adequate pressure?
>
> >
>
> > Thanks,
>
> > Greg
>
> >
>
> > Living Water Fire Protection
>
> > 1160 McKenzie Road
>
> > Cantonment, FL 32533
>
> > 850-937-1850
>
> > Fax: 850-937-1852
>
> >
>
> >
>
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> > To Unsubscribe, send an email
> > to:[EMAIL PROTECTED]
> > (Put the word unsubscribe in the subject field)
>
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> > To Unsubscribe, send an email
> > to:[EMAIL PROTECTED]
> > (Put the word unsubscribe in the subject field)
>
>
> -- 
> Best regards,
>  Charles                            mailto:[EMAIL PROTECTED]
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to