You're not missing anything.  The person specifying, designing, requiring this 
in the name of life safety is missing a sense of reality.
   
  The system will protect the steel at the top, and to some extent the steel 
walls.
   
  I guess to some extent it might protect firefighters.
   
  If there is a life safety issue, the specifier, designer, requirer should 
look for another code complying mitigation.

Richard Lindner <[EMAIL PROTECTED]> wrote:
  How effective are sprinklers located at a ceiling of a 70' high building?
The building is metal construction, nothing is really capable of burning.
Designing for light hazard. Sprinklers are being provided mainly for life
safety. What am I missing (ie it doesn't feel like its going to work).