The issue here is verifying both piping integrity and ability to flow system demand. How do you do that with air (you go for 500 cfm instead of gpm on the most remote standpipe -lol)?

Roland

On Jan 17, 2008, at 7:30 PM, [EMAIL PROTECTED] wrote:


The Oregon Fire Code allowed testing with air.



In a message dated 1/8/2008 4:41:40 P.M. Eastern Standard Time,
[EMAIL PROTECTED] writes:

We have been asked by our local AHJ what the std. procedure and costs are
for  testing of Dry Manual Standpipes in other jurisdictions.
They would like to  know the answers to the following questions:

1. Does your local fire dept. supply a engine to test dry manual standpipes?

2. or does a local contractor supply a pump with similar supply curve?

3. If local FDP  supplies engine do they charge for its use?

4. How much do they  charge?

5. Does the local FDP have a std. Wavier you sign before they test any
standpipe using their pumper?

6. Any other std practices  your local AHJ's use in testing Dry Manual
standpipes?

Thanks for  any help

Thom McMahon
Firetech, Inc.
2560 Copper Ridge  Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax:  970-879-7926

_______________________________________________
Sprinklerforum  mailing  list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:Sprinklerforum- [EMAIL PROTECTED]
(Put  the word unsubscribe in the subject field)







**************Start the year off right.  Easy ways to stay in shape.
http://body.aol.com/fitness/winter-exercise?NCID=aolcmp00300000002489
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:Sprinklerforum- [EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to