No hose requirement for NFPA 13R, but there is a fire flow demand in the IFC
in B.105.2 and Table B.105.1 (Outside hose allowance so to speak, may
require additional fire Hydrants)
Additionally you may require a standpipe in some 13R occupancy's, if it is
Automatic wet then you have an interior hose allowance, especially if you
have a combination standpipe.