Dears friends Craig, Travis, Kurt & Todd,
  Many thanks for your detailed answer, your answers were very helpful,.
  I will use the sprinkler piping for my fire hoses to save some pipe, after 
calculation, the water velocity in piping is about 20 ft/s and the capacity of 
sprinkler piping in each floor is 1030 gallons, so it seems that each floors 
needs 2 dry pipe systems (As NFPA limits the volume of a dry pipe system to 750 
gallons).
  ***I know that this 750 gallons limit may be exceeded if  the maximum water 
delivery time is less than 60 seconds, I will use accelerators to speed the 
operation of dry pipe systems, but I don't think even the accelerators can 
reduce it to 60 seconds because the system is large, what do you think? Do I 
have to use 2 dry pipe systems for each floor? Is there any solution to use 
only 1 dry pipe system for each floor as I want to be economical? Even if I 
don't connect fire hoses to sprinkler piping, the system is large enough and it 
doesn't help that much, any ideas?
   
  *** Another question is that, the garage lighting system is about 50 cm below 
the roof, can I place the sprinklers above the lighting? I think this is a kind 
of obstruction, what should I do? should i change the place of lighting system?
   
  Thanks,
  Reza
  

[EMAIL PROTECTED] wrote:
  Reza,


1- What is your recommended Area of sprinkler operation and Density
for my application after determining from the Density/Area curve? 
ANSWER: .15/1500 works but don't forget to increase the design area by
30% due to it being a dry system. So you would have .15/1950 sq. ft

2- I am going to use upright sprinklers, what kind of sprinkler is
more common for such an application? standards coverage/extended
coverage...?
ANSWER: Due to a lot of concrete structure and obstructions you will
most likely end up with standard coverage. But that depends on the
structure. 

3- What is the common distance between sprinklers and maximum area of
coverage per sprinkler for a parking garage?
ANSWER: Again this will depend on the structural design, 130 sq ft or
less would not be uncommon.

4- Is it necessary place a sprinkler exactly at above each car or not?
ANSWER: As answered, no.

5- Is it necessary to place sprinklers in corridors & ramps where no
cars are parked and only cars are moving?
ANSWER: Sprinkle throughout, that means every area.

6- What is the NFPA recommended duration for sprinkler system & inside
hose stream?
ANSWER: 250 gpm for hose stream, 90 minute duration, it can be 60
minutes if you have an alarm system monitoring the sprinkler system 7
days a week, 24 hours a day. 

7- Can I connect the inside hose to the dry sprinkler system piping?
or should I connect the inside hose piping directly to the fire pumps?
ANSWER: Either way. You just have to make sure you take the connection
point into consideration when you do your calculations. Using the
sprinkler piping would save some pipe.

8- I will place some inside fire hoses in the garage that provides 1
1/2 in. hose stations and according to NFPA-14 the minimum residual
pressure at the outlet of most remote 1 1/2 in. hose stations
should be 65 psi for hydraulically designed systems, so I think my fire
pump head should be at least 80 psi? What do you think about this
fire pump head, do you think it is low, high or good?
ANSWER: That can only be answered once you've performed your
calculations. Start there and make adjustments accordingly but
depending on the configuration of the system, that might be close or a
bit low to start with. Another thing to consider is will your fire
department use the 1 1/2" fire hoses or will they want to bring their
own hoses. If they prefer to provide their own, will they be 1 1/2" or
2 1/2" hoses? Here in the States we don't usually provide hoses since
most people would hurt themselves trying to act like a fireman. We
usually provide hose connections for the fire department to use. It is
a matter of whether you intend to have these hoses handled by non-fire
fighters or professional fire fighters. Plus hoses left in places like
this often are not tested regularly and can get dry rotted and not work
when needed. In some places they would also get stolen, especially the
nice shiny nozzles. Don't forget about considering fire extinguishers
if they are available. 

9- I want to protect both strories with a single riser using a 4" dry
pipe system to feed my sprinkler system & fire hoses, what do you think
about it?
ANSWER: See previous answer by Mr. Kingston. You will need to examine
fill times and the total size of the system in gallons. Also, if you
have the whole garage as one system, once the fire event is over or if
you have a false trip, you will have to drain the entire system. Also
if you have to take the system out of service for maintenance, the
entire system is disabled. If you segregate it into separate levels or
zones it will make maintenance simpler as well as your design effort.
Size of the system riser will again be determined when you run your
calculations. One other thing is due to the openings from level to
level, some would look at this as being one single fire zone. That
would be 88,000 sq. ft. as you've stated. With that in mind you can
only service 52,000 sq. ft per system. There are a lot of things that
will guide you in determining whether you go with one or more systems.





Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC 29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


       
---------------------------------
Looking for last minute shopping deals?  Find them fast with Yahoo! Search.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to