Subject: Parking Garage Sprinkler System

Hi All,
  I would like to ask about sprinkler system design in a car parking
garage. The parking garage has two stories (Basement & Ground floor). It
is only for car parking application which can hold about 350 cars.
  There is No mechanical devices to transport cars, and cars will drive
to their own parking palaces.
  The area of each story is about 44,000 square feet, and ceiling high
is about 10 feet.
  We are going to design a dry pipe sprinkler system for this car
parking garage as piping are subjected to freezing during the cold
weather.
   
  I looked up in NFPA codes for designing car parking garage, but I
couldn't find that much helpfull information in NFPA-88A.
   
  In NFPA-13 I saw that automobile parking and showrooms are specified
as 
  Ordinary hazard occupancies (Group 1).
   
  I am going to design a tree dry pipe sprinkler system & some inside
fire hoses in the garage.
   
  My questions are as followings:
   
  1- What is your recommended Area of sprinkler operation and Density
for my application after determining from the Density/Area curve?
   
  2- I am going to use upright sprinklers, what kind of sprinkler is
more common for such an application? standards coverage/extended
coverage...?
   
  3- What is the common distance between sprinklers and maximum area of
coverage per sprinkler for a parking garage?
   
  4- Is it necessary place a sprinkler exactly at above each car or not?
   
  5- Is it necessary to place sprinklers in corridors & ramps where no
cars are parked and only cars are moving?
   
  6- What is the NFPA recommended duration for sprinkler system & inside
hose stream?
   
  7- Can I connect the inside hose to the dry sprinkler system piping?
or shoud I connect the inside hose piping directly to the fire pumps?
   
  8- I will place some insde fire hoses in the garage that provides 1
1/2 in. hose stations and according to NFPA-14 the minimum residual
pressure at the outlet of most remote 1 1/2 in. hose stations should be
65 psi for hydraulically designed systems, so I think my fire pump head
should be at least 80 psi? What do you think about this fire pump head,
do you think it is low, high or good?
   
  9- I want to protect both strories with a single riser using a 4" dry
pipe system to feed my sprinkler system & fire hoses, what do you think
about it?
   
  Thanks for your kind help in advance,
  Reza
   

       
---------------------------------
Looking for last minute shopping deals?  Find them fast with Yahoo!
Search.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to