Forum,

I have a client that would like to install an isolation control valve
several feet downstream of a preaction valve.  The system is double
interlock.  The purpose of the valve would be to permit a full flow trip
test, per 25, without flooding the system piping.  The system protects a
Tier III data center and they are not going to allow flooding of the piping
if there are other options available.  How common is this arrangement?  Any
pitfalls?

Thanks

Ray Schmid, P.E.
President 
Schmid & Associates, PC
Fire Protection Engineers
443-465-4206
[EMAIL PROTECTED]
 
This communication is confidential. This information may be privileged and
is intended for the exclusive use of the above named addressee(s). If you
are not the intended recipient(s), you are expressly prohibited from
copying, distributing, disseminating, or in any other way using any of this
information contained herein. If you have received this communication in
error, please contact the sender by telephone at (443) 465-4206 or respond
via e-mail and then permanently delete the original email and any copies.


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to