Use 0.10 density over the room, or the head listing, whichever is greater. If you head is protecting 20'x12' then the area is 240 sq ft. At 0.1 gpm, the requirement is 24 gpm. A 4.9k head at 20x20 is 20 gpm, so you use the 24 gpm.
If the head was protecting 20'x6', then you would use the listing of the head at 20 gpm. -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Brian Harris Sent: Friday, February 15, 2008 6:20 AM To: [email protected] Subject: Residential Sprinklers in a 13 System Somebody help a rookie out...... This is the 1st time I've used Residential heads in a 13 system and I want to make sure my calc's are right, I'm not totally clear on 11.3.1.2 (07). What density do I need to use? Any other "catches" I should know about? Regards, <http://www.firstdefensefire.com/> __________ NOD32 2879 (20080215) Information __________ This message was checked by NOD32 antivirus system. http://www.eset.com _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)