Use 0.10 density over the room, or the head listing, whichever is greater.

If you head is protecting 20'x12' then the area is 240 sq ft.  At 0.1 gpm,
the requirement is 24 gpm.  A 4.9k head at 20x20 is 20 gpm, so you use the
24 gpm.

If the head was protecting 20'x6', then you would use the listing of the
head at 20 gpm. 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian Harris
Sent: Friday, February 15, 2008 6:20 AM
To: [email protected]
Subject: Residential Sprinklers in a 13 System

Somebody help a rookie out...... This is the 1st time I've used Residential
heads in a 13 system and I want to make sure my calc's are right, I'm not
totally clear on 11.3.1.2 (07). What density do I need to use? Any other
"catches" I should know about?
 