FM undertook a reliability study about 10 years ago, based on results of pump tests during inspections and loss information. The results were interesting in that the electric pumps were more reliable when tested, but were much more likely to fail during a fire due to power loss resulting from the fire or "pulling the plug" on the main supply for safety sake. The net result was that diesel pumps are more reliable overall, but only so long as they are properly tested and maintained.

As regards diesel/generator sets, it turns out that the weak link is the transfer switch. The transfer switch can not only fail to operate when power is lost, but also can fail when there is no power loss, preventing the pump from running. The net result is that the electric pump with diesel backup is probably less reliable than either an electric pump or a diesel pump alone. It certainly isn't worth the large extra expense in terms of reliability.

Joe

Charles Thurston wrote:
Hello sprinklerforum,

  I am looking for opinions on installing a Diesel fire pump Vs installing
  an Electric fire pump and Gen Set. I have a location that is being
  cut loose from the "Site Wide" fire pump loop now owned by others.


_______________________________________________