See the June 2006 Edition of "Sprinkler Age" in the article "Balconies and the 
IBC" by Steve Rians.

Mike Brown




-----Original Message-----
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Ken Holsopple 
(forum)
Sent: Friday, February 22, 2008 9:51 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Dry HSW under open framed 2x's

To all....

Looking at A.8.14.7 in 13 (02 ed), it looks like you are allowed to angle (@
a 45ºangle) a dry pendent through the wall without regard to construction
type. What would be the downside to doing this with a sidewall? (Other than
it does not show an HSW in the picture) Wouldn't the spray pattern develop a
little better?

Ken Holsopple
Rowe Sprinkler Systems, Inc.


I'm noticing a lot of small exterior canopies being protected with dry
horizontal sidewall
sprinklers even though it is open framing (usually 2X6's or 2X10's at 24"
o/c) without any type of material fastened to the underside of this framing
- which is all good and well since it mostly complies with NFPA #13 '07 ed
section 8.4.2 except that it's not 'SMOOTH.' So I guess that's my question,
they aren't smooth so how are people getting away with this? Smooth being
defined as sructural members being spaced more than 7'-6" o/c. per A3.7.2.
   
  The only thing I can come up with is A8.15.7 where you can install a
*pendant* at a 45 degree angle to protect small unheated areas so if it's
okay for a pendant why not a HSW? (I'm sure it has to do with the
intracacies of unfamiliar testing and listing requirements of a pendant over
a hsw???)
   
  Any thoughts?
   
  Thx,
  -B-
   
   
  Below are the sections talked about:
   
  NFPA #13 2007 ED.
8.4.2 Sidewall Spray Sprinklers. Sidewall sprinklers shall only be installed
as follows:     
(1)  Light hazard occupancies with smooth, horizontal or sloped, flat
ceilings
(2)  Ordinary hazard occupancies with smooth, flat ceilings where
specifically listed for such use
(3)  To protect areas below overhead doors
   
   
  A.8.15.7  Small loading docks, covered platforms, ducts, or similar small
unheated areas can be protected by dry-pendent sprinklers extending through
the wall from wet sprinkler piping in an adjacent heated area. Where
protecting covered platforms, loading docks, and similar areas, a dry
pendent sprinkler should extend down at a 45 degree angle. The width of the
area to be protected should not exceed 7½ ft (2.3 m). Sprinklers should be
spaced not over 12 ft (3.7 m) apart. (See Figure A.8.15.7.)
  
 
  A.3.7.2
(3)  Smooth Ceiling Construction. The term smooth ceiling construction as
used in this standard includes the following: 
(a)  Flat slab, pan-type reinforced concrete
(b)  Continuous smooth bays formed by wood, concrete, or steel beams spaced
more than 7½ ft (2.3 m) on centers - beams supported by columns, girders, or
trusses
(c)  Smooth roof or floor decks supported directly on girders or trusses
spaced more than 7½ ft (2.3 m) on center
(d)  Smooth monolithic ceilings of at least ¾ in. (19 mm) of plaster on
metal lath or a combination of materials of equivalent fire-resistive rating
attached to the underside of wood joists, wood trusses, and bar joists
(e)  Open-web-type steel beams, regardless of spacing
(f)  Smooth shell-type roofs, such as folded plates, hyperbolic paraboloids,
saddles, domes, and long barrel shells
(g)  Suspended ceilings of combustible or noncombustible construction
(h)  Smooth monolithic ceilings with fire resistance less than that
specified under item (d) and attached to the underside of wood joists, wood
trusses, and bar joists 

       
---------------------------------
Looking for last minute shopping deals?  Find them fast with Yahoo! Search.
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to