We had the same situation in a condo and contacted the sprinkler manufacturer. In our case we put heads under the light cove to cover the "shadow" and the sidewall protected the center of the room. This was approved by the manufacturer as far as their input goes. The AHJ also accepted this.
Thank you, Greg McGahan Living Water Fire Protection, LLC 1160 McKenzie Road Cantonment, FL 32533 850-937-1850 Fax: 850-937-1852 -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Todd Williams - FPDC Sent: Tuesday, February 26, 2008 7:01 AM To: [email protected] Subject: obstructions below sidewalls I have run into a couple of situations lately where there have been continuous obstructions directly below sidewall sprinklers that extend from the wall the sidewall is fed from. The latest is a light cove that sticks out 11" from the wall and is 8" below the sprinkler. I can't find anything in 13 that discusses or would relate to this. Most of the discussion in 8.7.5.2.1 related to "dry shadow" in front of and not underneath. Am I missing something? Any thoughts? Todd G. Williams, PE Fire Protection Design/Consulting Stonington, Connecticut www.fpdc.com 860.535.2080 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)