I have never done a chemical processing facility that fell under NFPA 13
and never an OH occupancy. Usually they fall under NFPA 30 or a more
stringent and specific FM criteria.  Each plant requires a detailed
hazards analysis of the process, equipment types and purpose, MSDS info
as well as building construction among other issues to determine the
proper protection approach.  

The other issue is that there are new technologies being born every day.
Each new product being used or produced doesn't always have a page of
it's own in the code.  So it takes some homework and detailed analysis
when it comes to determining fire protection criteria for these kinds of
facilities.  

"Ya gotta love it!"


Craig L. Prahl, CET   
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams - FPDC
Sent: Thursday, March 06, 2008 11:26 AM
To: [email protected]
Subject: Ordinary chemical plants?

In NFPA 13, under the section describing OH2 occupancies, they mention
"Chemical plants - ordinary". What is an ordinary chemical plant?

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to