The exception says that sprinklers may be excepted where there is no
"... storage or handling of combustibles."   You may not have storage,
but you sure do have handling.   I believe the wording of the exception
was very carefully chosen so that loading dock overhangs would still
require sprinklers.

Steve Leyton
Protection Design & Consulting


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Greg
McGahan
Sent: Monday, March 10, 2008 1:04 PM
To: [email protected]
Subject: non-combustible overhangs


I am just checking myself here; but if you have a non-combustible
overhang
over 4' wide (actually about 6')under which 18 wheelers back up and
unload,
are sprinklers required? These are box trucks and they carry carpet. The
carpets are really never exposed as they go straight from truck to
warehouse.

What say ye learned ones?

Thank you,
Greg McGahan