The Reliable F1 Res 49 is listed for an 8 inch deflector distance but the 
problem with all residential sprinklers is that they are not listed for 
obstructed construction which you may find in an attic.  NFPA 13D addresses it 
by saying that you can install pendent residential basements where it is 
expected that a ceiling will be installed or something like that.  To my 
knowledge there is no residential upright sprinkler made.  In my opinion you 
are better off using a Quick Response Commercial Upright sprinkler.

Mike Brown

-----Original Message-----
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Dennis J Briggs 
Jr.
Sent: Wednesday, March 12, 2008 2:18 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Residential Upright

Thanks Ron that may work for me.

Dennis Briggs, Jr.
Miller Fire Protection Inc.
2750 Marble Ct.
Forestville MD. 20747
Office - (301) 736-3000
Cell - (240) 304-8967
-----Original Message-----
From: Fletcher, Ron [mailto:[EMAIL PROTECTED]
Sent: Wednesday, March 12, 2008 01:13 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Residential Upright

I don't know of an upright but I think Globe makes a residential pendent listed 
for 8" or 12" deflector distance, I can't remember for sure. We have used them 
in loft style exposed systems because of the problem achieving the 4" deflector 
distance listed for most residential heads. Good luck. Ron Flecher Aero 
Automatic Phoenix, AZ -----Original Message----- From: [EMAIL PROTECTED] 
[mailto:[EMAIL PROTECTED] On Behalf Of Dennis J Briggs Jr. Sent: Wednesday, 
March 12, 2008 5:37 AM To: sprinklerforum@firesprinkler.org Subject: 
Residential Upright Does anyone know if there is a Listed Residential Sprinkler 
Head currently on the market and if so where i may find it. Thanks, Dennis 
Briggs, Jr. Miller Fire Protection Inc. 2750 Marble Ct. Forestville MD. 20747 
Office - (301) 736-3000 Cell - (240) 304-8967 
_______________________________________________ Sprinklerforum mailing list 
Sprinklerforum@firesprinkler.org 
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, 
send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject 
field) _______________________________________________ Sprinklerforum mailing 
list Sprinklerforum@firesprinkler.org 
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, 
send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject 
field)
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to