Never really noticed that before, on a calc I just looked at, a demand calc,
the continuation pressure is the same as pump outlet and system pressure,
probably churn plus city. It may reflect the max available? Ask Hydracalc or
check the documentation.
Bill Minkel, Designer
Western States Fire Protection, Dallas
NFPA Member #2578666

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of IPA
Sent: Thursday, March 13, 2008 3:00 PM
To: sprinklerforum
Subject: Pump "Continuation Pressure" in HydraCalc

Can anyone explain the concept of "contination pressure" to me regarding
fire pumps. The first time I've seen this term is in Hydracalc and I really
don't grasp it. Let' say I have a pump rated 125 psi @ 1000 gpm. (churn is
at 147 psi) my system demand is 98 psi @ 481 gpm at the pump discharge. The
report spits out the proper system demand pressure followed by:
"Continuation Pressure: 186.7, Pressure @ pump outlet 186.7 Pressure from
pump curve: 146.0" etc...

Any hydracalcers care to take a stab at this? Am I missing something, doing
something wrong, or is it too close to friday? I always thought max pressure
would be the pumps churn - not a continuation of pressure off the curve
somewhere in space?

Thanks in advance,
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to