If the alarm line is passing water and the alarm valve is not open, the
clapper is not seated.
The only time water enters the alarm line port is when the clapper is up, or
not seated.
Take off the cover, lift up the clapper and look at the seat(s) and the
rubber gasket on the clapper.
You might have to hand cut a replacement.  It's probably cut, warped or
damaged.
Tom
GRS


Am I allowed to respond to my own question?

The alarm valve leakage resulted in the drain pipe from the water motor gong
filling with rust.  I suspect that the water flowing through the retard
chamber may have caused the rust hole to form in the retard chamber. We now
have a new retard chamber, new restriction device, new water motor gong, new
drain pipe.  We still have water trickling through the restriction and out
the drain pipe.  At present I have the alarm valve closed, so we have no
leakage, but we also have no alarm notification.  Any ideas how to fix this
problem?

We have an old Star 4-175-D wet valve that is leaking through the alarm
valve.  when the valve is open, we get a trickle of water into the water
motor gong.  Not enough flow to trip the gong, but enough to rust the pipe
shut.  I do not find any info on this valve on the Tyco web site.

Does someone have a tech sheet you could send to me?

Douglas Hicks
General Fire Equipment Co of Eastern Oregon,Inc
541.377.1143 cell


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to