Any movement that does not damage the system or any part of the structure or
other systems is acceptable by code. If the owner is concerned about the
movement the pipe could be braced, similar to seismic. The standard is the
minimum, can you do more? YES!
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message -----
From: <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Sunday, March 23, 2008 5:11 PM
Subject: Dry System Movement During Trip Test
Dry systems tend to move around during the trip phase. Are there any
guidelines to be able to say "too much movement - add some additional
bracing"? Or, is any movement acceptable as long as the system stays
intact?
Bill Brooks
William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146
410-544-3620 Phone
410-544-3032 FAX
412-400-6528 Cell