Bill,
It does not mean no aisle jump. In the tests that Class I-IV protection
are based on, a test was considered successful even if ignition occurred
across the aisle but was contained (did not burn through to the other
side) of the target rack.
Joe
[EMAIL PROTECTED] wrote:
What is the minimum aisle width in order to use the ceiling only
densities for miscellaneous rack storage (Chap 13 - 2007)? Aisle widths
are specified in Chapter 16 but not in Chapter 13. Would this width be
3.5 ft per 3.9.3.7.5?
I'm assuming this would mean there's no ignition across a 3.5 ft aisle
if Table 13.2.1 is applied.
Bill Brooks
William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.