Bill,
It does not mean no aisle jump. In the tests that Class I-IV protection are based on, a test was considered successful even if ignition occurred across the aisle but was contained (did not burn through to the other side) of the target rack. Joe

[EMAIL PROTECTED] wrote:
What is the minimum aisle width in order to use the ceiling only
densities for miscellaneous rack storage (Chap 13 - 2007)?  Aisle widths
are specified in Chapter 16 but not in Chapter 13.  Would this width be
3.5 ft per 3.9.3.7.5?

I'm assuming this would mean there's no ignition across a 3.5 ft aisle
if Table 13.2.1 is applied.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146
410-544-3620 Phone
410-544-3032 FAX
412-400-6528 Cell

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to