We adopted a sprinkler ordinance in January for SFD’s and now are dealing
with some of the vacant lots in town that have a ¾” copper water service
lateral with a 1” meter.

Our Water Department (regulates from the corporation stop to the customer
side of the meter) has a maximum velocity standard of 15 feet per second.
When you flow 26 gpm through a ¾ inch service lateral the velocity is in the
30 fps range.

I am proposing we stay with NFPA 13D, the guiding design standard for
residential sprinklers in SFD’s. 13D does not seem to have a velocity
requirement and does allow ¾” pipe as long as hydraulically the pressure and
flow is available.

New subdivisions will have a 1.5” lateral so we won’t have the problem in
the future.

Has anyone ran into the velocity issue for residential 13D systems?

If so, were you successful in getting around the hurdle?

We do not believe exceeding the velocity in ¾” copper for a test and
possible fire will be an issue.

Thanks for any information you have.

Mark

 