With IIIB's and other chemicals stored either palletized or on shelves,
sometimes the hazard becomes the storage container moreso than the
content of the container.  When these kinds of situations arise where
the direction is unclear you may end up protecting the space based on
the combustible storage characteristics of the plastic containers. 

IIIB's usually don't create a lot of excitement as long as you're under
the IBC limits, and for IIIB's it's alot.  



Craig L. Prahl, CET   
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Sean
Conlin
Sent: Thursday, April 03, 2008 2:40 PM
To: [email protected]
Subject: RE: motor oil

Todd,

2003 ed.

I guess I jumped the gun, my reference was for rack storage which I'm
sure you've used before.  I don't recall seeing any reference for
palletized storage of IIIB's in NFPA 30

I know FM DS 7-29 has a few tables for plastic containers.  Good luck.

Sean



-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams
- FPDC
Sent: Thursday, April 03, 2008 11:23 AM
To: [email protected]
Subject: RE: motor oil

Sean,

Which edition of 30 are you using?

Todd


At 10:34 AM 4/3/2008, you wrote:
>Todd,
>
>Check out NFPA 30, Table 6.8.2.(e).
>
>Sean Conlin
>
>-----Original Message-----
>From: [EMAIL PROTECTED]
>[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams
>- FPDC
>Sent: Thursday, April 03, 2008 8:59 AM
>To: [email protected]
>Subject: motor oil
>
>I was at a location the other day that had pallets of motor oil (Class 
>IIIB liquid) in quart and gallon plastic containers stacked 1 high (5 
>ft). I have never evaluated this specific commodity before so I started

>my search from scratch. There seems to be nothing in NFPA
>13 that addresses it, so I went to NFPA 30. the but the best I could 
>find there was small metal containers of IIIB. Since this type of stuff

>is all over the place, I would assume that this has had to be 
>evaluated, but I can't find any resource. Any help?
>
>Todd G. Williams, PE
>Fire Protection Design/Consulting
>Stonington, Connecticut
>www.fpdc.com
>860.535.2080
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>To Unsubscribe, send an email 
>to:[EMAIL PROTECTED]
>(Put the word unsubscribe in the subject field)
>
>
>--
>No virus found in this incoming message.
>Checked by AVG.
>Version: 7.5.519 / Virus Database: 269.22.5/1357 - Release Date: 
>4/3/2008
>10:48 AM
>
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>To Unsubscribe, send an email 
>to:[EMAIL PROTECTED]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


--
No virus found in this incoming message.
Checked by AVG. 
Version: 7.5.519 / Virus Database: 269.22.5/1357 - Release Date:
4/3/2008
10:48 AM


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to