Travis,

You'll have to look at the concealed space requirements in NFPA 13 and see if it conforms. I believe that the insulation exception is a special case because it is not a hard, fixed surface. I've had to do under catwalks in the past, so you might.

My brain cooked about noon today.

Todd


At 06:07 PM 4/4/2008, you wrote:
I am working on a project where there is a decent sized attic (21' above the
ceiling at the peak).  The drop ceiling is 2' below the bottom of the
trusses.  I have sprinklers at the roof deck and in the ceiling.  However,
there is a walkable plywood deck placed on the bottom chord throughout a
large portion of this attic.  Will I need to add another level of sprinklers
in the space between the walkable plywood and the ceiling?  I know you don't
have to add sprinklers in the "interstitial" space between insulation placed
between joists and the ceiling if you have sprinklers at the roof deck.
But, I don't know if this would be a similar scenario to allow for the
sprinklers to be left out.  I am brain dead on a Friday and not sure today.

Thanks in advance for your help!

Travis

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080 _______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to