Brian, 1.) It seems fairly common on 13R designs to use heads that need pressures over 7 PSI. If this is true in your case, can you switch to a different head? 2.) Sometimes you can easily make a conversion to a grid system without too much pain and that may help. Kurt Kingston Commercial Fire Protection Inc. ph (360)-848-9093 fax (360)-848-1072 -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Brian Harris Sent: Monday, April 07, 2008 11:31 AM To: [email protected] Subject: Failed Bucket Test
Fellow forum people: I have a situation where we have designed and installed a 13R system, it is completely finished and wham-o we fail the bucket test! Our system was designed based on the flow test provided by the city fire dept., turns out that a test taken now with the failed test shows a 25% drop in static & residual pressures, hence the failed test. Of course the owner is looking to us to pull a magic rabbit out of our #$% , err I mean hat, we have tried a few different things but with that big of a pressure loss there's really not much we can do. I don't feel it's our liability at this point since we went off the city's water flow test and per the calc's we were good, any thoughts? Regards, <http://www.firstdefensefire.com/> E-mail message checked by Spyware Doctor (5.5.0.178) Database version: 5.09560 http://www.pctools.com/spyware-doctor/ _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)