On Apr 8, 2008, at 10:03 AM, Roland Huggins wrote:

A concealed space with a height less than 36 inches (as well as a few other parameters such as a combustible upper surface) requires a specific listing for concealed spaces (13:8.15.1.6 07 edition).

Roland

On Apr 8, 2008, at 9:27 AM, Ron Greenman wrote:

As far as I know the only time you need specifically listed concealed space sprinklers is when you're protecting plastic pipe in combustible spaces with sprinklers attached to the plastic pipe. Since I'd only be using dry heads in unheated spaces I'd presume a dry system which you can't use for dry systems or coming from pipe in a heated space to protect an unheated space so no plastic to protect. Educate me if I'm missing something.