Yes on sprinkler, Yes on the dry sidewall since the cooler is part of and connects to the protected building, technically its part of the building so treat it like a room of that building. On the other hand an independent structure with no openings into the protected building and a rated exterior wall is another subject.
John Drucker Fire Protection Subcode Official (AHJ) New Jersey -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Todd Williams - FPDC Sent: Tuesday, April 08, 2008 4:46 PM To: [email protected] Subject: cooler A cooler outside the building envelope, but opens into the space. Sprinkler or no? If yes, would a dry sidewall into the cooler be acceptable? Otherwise you would have to run an anti-freeze or small dry system with pipe outside the building. Todd G. Williams, PE Fire Protection Design/Consulting Stonington, Connecticut www.fpdc.com 860.535.2080 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)