You would never use beam detectors in a garage and especially in an open structure like this. Consider the fact that cars emit smoke and other exhaust gases, the detectors would be alarming all the time.
AS in the area is all you should need. The area is heated right? Also in some jurisdictions, (rain) water run off from cars is routed to oil separators before being discharged into the sanitary or storm sewers. Make sure someone has verified that the drains could handle the discharge from the calculated sprinkler flow. Otherwise you could end up with an underground pool and lots of flooded cars. Even though this is more of a plumbing issue. It's a good idea to send an e-mail notifying someone of the potential problem. Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [EMAIL PROTECTED] http://www.ch2m.com -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Haji, Jaber M Sent: Tuesday, April 08, 2008 8:24 AM To: [email protected] Subject: High Rise Bldg An existing high rise building with a basement is utilized a parking garage, such parking garage is protected by wet type sprinkler system, someone asked for a beam type smoke detectors in such area, your insight is needed, is it really required by IBC/IFC or NFPA or the existing AS will be adequate? _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)