Some res heads will let you go 8" below the ceiling. With a 6" beam, stick one in the beam and let it go.
-----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Bob Knight Sent: Tuesday, May 06, 2008 12:52 PM To: [email protected] Subject: Residential Sprinklers and Beam Obstructions I'm working on a home (13D) that has several rooms with the ceiling broken up by "beam pockets". These vary in width from 2'8" to 3'3" o.c. with the beams being 6" deep. Concealed residential sprinklers are being used. In one room, which is 224 sf, if I place a sprinkler in every pocket like I think I should, there will be 13 sprinklers. This averages out to 17 sf per head. Another room is 375 sf and will require 10 sprinklers. This averages at 37.5 per head. In rooms of this size do I really need a sprinkler in every pocket? Can a sprinkler be placed in every other pocket and be acceptable? Has anyone else found a better way to protect rooms like this? Any and all suggestions will help. Thanks, Bob Knight, CET (208) 318-3057 [EMAIL PROTECTED] www.firebyknight.com _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)