After doing the math the pressure loss can be accounted for by the
change in elevation and the loss through the backflow at the low flow.
I was unaware of the loss in pressure with no/little flow on the BFP.
Thanks for everyone's input on the matter.
Dewayne 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Dewayne
Martinez
Sent: Friday, May 09, 2008 1:59 PM
To: [email protected]
Subject: RE: Change in static pressure

Thanks,
I will look into the cut sheet.  The fitter preformed an alarm test so
only a small amount of water was flown. 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Paul
Pinigis
Sent: Friday, May 09, 2008 1:22 PM
To: [email protected]
Subject: RE: Change in static pressure

Look at the cut sheet on the BFP.  Some BFPs require a significant
amount of pressure to open at very low flows.  For example, an 12" Ames
2000SS requires almost 6 psi to operate at very low flow so it can sit
there all day with an upstream pressure nearly 6 psi higher than the
system side pressure.  

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Dewayne
Martinez
Sent: Friday, May 09, 2008 1:55 PM
To: [email protected]
Subject: Change in static pressure

I have a job site which is 10ft higher than the water supply.  A gauge
on the water supply hydrant reads 55 PSI static pressure while two
gauges on the system riser after the BFP read 37 PSI?  The total
elevation change between the system gauges and the supply gauge is about
17ft.  Why would there be a 18 PSI difference between the gauges when
elevation only accounts for 7.36 PSI? 
I confirmed with the city that there are no shut valves.  Any thoughts? 
Thanks,
Dewayne
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to