Actually, we've been requested to provide As-Builts because a head was 12" different from where shown on plan (HVAC conflict and still well within calculated spacing requirements) and because hangers were not shown exactly on the pipe where they were shown on the plan.?? In the past we figured on As Builts for substantial changes to the plan, but in the last few years, the Inspectors are increasingly unwilling (or unable) to approve those changes in the field at the time of inspection.? Plans must be resubmitted, re-checked and then reinspected at a delay of? weeks, if not months for minor changes which do not affect design or system operations.
R. Huerta -----Original Message----- From: Roland Huggins <[EMAIL PROTECTED]> To: [email protected] Sent: Mon, 28 Apr 2008 7:56 am Subject: Re: As-Built Documentation Actually 25 says they shall be maintained. It is understood by 25 that they shall be provided.? ? As already identified 14.1.2 indicates t as well as the CMTC under Plans states Installation conforms to accepted plans.? ? I doubt that a new set of calculations is performed for a couple of elbows (that's one of the reasons to leave a margin).? ? Roland? ? On Apr 27, 2008, at 4:36 PM, Mark Hasenmyer wrote:? ? > Bill:? >? > 2006 IFC also references 2002 NFPA-25; see 4.6. NFPA-13 18.1 says > that? > sprinklers systems must comply with NFPA-25 and NFPA-25 4.6 requires? > as-builts.? >? > Mark Hasenmyer, PE? > MEH Fire Protection Engineering LLC? > 1311 River Oaks Drive? > Flower Mound, TX 75028? > Office (972) 874-2662? > Fax (972) 874-5591? >? >? > -----Original Message-----? > From: [EMAIL PROTECTED] > [mailto:[EMAIL PROTECTED] On Behalf Of? > [EMAIL PROTECTED] > Sent: Sunday, April 27, 2008 6:18 PM? > To: [EMAIL PROTECTED] > Subject: RE: As-Built Documentation? >? > 2002, referenced by 2006 IBC.? >? > Bill Brooks? >? > William N. Brooks, P.E.? > Brooks Fire Protection Engineering Inc.? > 372 Wilett Drive? > Severna Park, MD 21146? > 410-544-3620 Phone? > 410-544-3032 FAX? > 412-400-6528 Cell? >? > -------- Original Message --------? > Subject: RE: As-Built Documentation? > From: "John Drucker" <[EMAIL PROTECTED]>? > Date: Sun, April 27, 2008 12:28 pm? > To: <[email protected]>? >? > Which edition ?? >? > -----Original Message-----? > From: [EMAIL PROTECTED] > [mailto:[EMAIL PROTECTED] On Behalf Of? > [EMAIL PROTECTED] > Sent: Sunday, April 27, 2008 11:10 AM? > To: [EMAIL PROTECTED] > Subject: As-Built Documentation? >? > Would you say NFPA 13 "requires" as-built drawings and calculations?? >? > I know 99.9% of the systems are installed exactly like the shop? > drawings. But, for that other 0.1%, is it necessary to do an as-built? > calculation to match the as-built drawing? It seems NFPA 13 is > based on? > the 99.5% and is silent about what documentation is required when > field? > changes occur during installation.? >? > Bill Brooks? >? > William N. Brooks, P.E.? > Brooks Fire Protection Engineering Inc.? > 372 Wilett Drive? > Severna Park, MD 21146? > 410-544-3620 Phone? > 410-544-3032 FAX? > 412-400-6528 Cell? >? >? >? > _______________________________________________? > Sprinklerforum mailing list? > [EMAIL PROTECTED] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum? >? > To Unsubscribe, send an email? > to:[EMAIL PROTECTED] > (Put the word unsubscribe in the subject field)? >? > _______________________________________________? > Sprinklerforum mailing list? > [EMAIL PROTECTED] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum? >? > To Unsubscribe, send an email? > to:[EMAIL PROTECTED] > (Put the word unsubscribe in the subject field)? >? >? > _______________________________________________? > Sprinklerforum mailing list? > [EMAIL PROTECTED] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum? >? > To Unsubscribe, send an email to:Sprinklerforum-> [EMAIL PROTECTED] > (Put the word unsubscribe in the subject field)? >? > _______________________________________________? > Sprinklerforum mailing list? > [EMAIL PROTECTED] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum? >? > To Unsubscribe, send an email to:Sprinklerforum-> [EMAIL PROTECTED] > (Put the word unsubscribe in the subject field)? >? ? _______________________________________________? Sprinklerforum mailing list? [EMAIL PROTECTED] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum? ? To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)? _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)