We've done several 13R systems and yes, they usually double the design area to 8 sprinklers. Even when the largest compartment may have only 2 or 3.
Steve Leyton Protection Design & Consulting -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Gregg Key Sent: Wednesday, May 21, 2008 6:11 AM To: [email protected] Subject: Re: unified facilities criteria question Which brings up another interesting question. Since UFC 3-600-01 requires a higher hose flow for all of the hazards, does the higher flow apply to 13R systems? the increased area does not apply due to the specific requirement of calculating 4 sprinkler heads, but how is the higher requirement for hose stream accounted for? Thom McMahon wrote: > We just finished a layout for NAVFAC PACDIV, for a 2 story dorm. > Poured concrete construction, full height concrete walls, floors and > roof, every 24'-0" with only 30'-0" front to back.(5200 Sf per floor > total) UFC say's you can use 13R, NAVFAC say's NO. UFC say's reduced > area for QR heads, NAVFAC say's NO. So we have a two story concrete > dorm with a 3000SF design area, 250 GPM hose at the base of riser, and > 6" riser and 4" mains, for a job where if we flowed every head between > the concrete walls (6) and were overflowing 4 of them, we'd still only need a 3" underground, with 2" > mains. Your Tax $$$ at work. > > -----Original Message----- > From: [EMAIL PROTECTED] > [mailto:[EMAIL PROTECTED] On Behalf Of Vince > Sabolik > Sent: Tuesday, May 20, 2008 7:47 AM > To: [email protected] > Subject: RE: unified facilities criteria question > > Ed -- > > I wasn't able to use small room at a USMC facility recently, in fact > they required > a base of 3.000 sf for a wet system. You are however allowed to > discount for use of QR heads applied to that 3,000 sf. > > You can look this up in Table 4-1 in the Unified Facilities Criteria > "Fire Protection Engineering for Facilities" > > > > Vince > > > > > At 09:26 AM 5/20/2008, you wrote: >> In my opinion, the small room rule can be used. I believe the 225 sq >> ft and 130 sq ft limits are there to restrict the use of special >> sprinklers, not to limit the use of other NFPA 13 spacing rules. >> >> Bill Brooks >> >> William N. Brooks, P.E. >> Brooks Fire Protection Engineering Inc. >> 372 Wilett Drive >> Severna Park, MD 21146 >> 410-544-3620 Phone >> 410-544-3032 FAX >> 412-400-6528 Cell >> >> -------- Original Message -------- >> Subject: unified facilities criteria question >> From: "Tambini, Ed" <[EMAIL PROTECTED]> >> Date: Tue, May 13, 2008 5:24 pm >> To: <[email protected]> >> >> to all the armed forces people out there: >> >> the UFC 3-600-01 4-2.3.6 lists sprinkler coverage areas to be in >> accordance with NFPA 13 except that they must not exceed 225 sq ft >> for light hazard areas and 130 sq ft for ordinary hazard. This >> effectively rules out extended coverage sprinklers, but does it also >> rule out the small room rule for light hazard areas? >> >> thanks, >> ed >> aero >> _______________________________________________ >> Sprinklerforum mailing list >> [email protected] >> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum >> >> To Unsubscribe, send an email >> to:[EMAIL PROTECTED] >> (Put the word unsubscribe in the subject field) >> >> >> _______________________________________________ >> Sprinklerforum mailing list >> [email protected] >> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum >> >> To Unsubscribe, send an email >> to:[EMAIL PROTECTED] >> (Put the word unsubscribe in the subject field) > > Vince Sabolik > Christi Fire Protection, Inc. > 11351 Pearl Road > Strongsville, Ohio 44136 > > T 440 572-7730 F 440 572-7719 Email: > <mailto:[EMAIL PROTECTED]>[EMAIL PROTECTED] > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > To Unsubscribe, send an email > to:[EMAIL PROTECTED] > (Put the word unsubscribe in the subject field) > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > To Unsubscribe, send an email > to:[EMAIL PROTECTED] > (Put the word unsubscribe in the subject field) > > _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)