Todd, can the branchlines on one slope be staggered from the branchlines on
the other slope?  If possible, this would increase the straight line
distance.

Ed Kramer
Littleton, CO

 
> I am working on a historic church sanctuary with a pitch of
> approximately 28/12. The arrangement calls for branch lines to be
> symmetrical on each side, similar to NFPA 13 (2002) figure
> 8.6.4.1.3.1(b). I can meet the requirements for the steeply pitched
> roof section 8.6.4.1.3.3 and my "S" distance over the peak is good,
> but my straight line distance between sprinklers would be less than 6
> ft and the deflectors would be effectively pointing the discharge
> towards the sprinkler on the opposite side. I think I have a problem
> here, but I am not sure how to address it. Any thoughts?
> 
> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, Connecticut
> www.fpdc.com
> 860.535.2080