7.10.1.2.3 says to the "required flow" not to exceed 1250, in this case the required is 1000 gpm per 7.10.1.1.3
R/ Matt Matthew J. Willis Living Water Fire Protection, LLC. 1160 McKenzie Rd. PO Box 877 Cantonment, FL. 32533 850-937-1850 Voice 850-937-1852 Facsimile [EMAIL PROTECTED] ----- >-----Original Message----- ----- >From: [EMAIL PROTECTED] ----- >[mailto:[EMAIL PROTECTED] On ----- >Behalf Of Dewayne Martinez ----- >Sent: Thursday, May 29, 2008 4:13 PM ----- >To: [email protected] ----- >Subject: Max flow for class I standpipes ----- > ----- >What is the max flow for class I standpipes in a fully ----- >sprinklered building? I have 4 in a building and have ----- >been taught in the past to only calculate 1000 gpm max ----- >(7.10.1.1.3, NFPA 14 (03 ed)) but section ----- >7.10.1.2.3 seems to contradict this. ----- >Thanks, ----- >Dewayne ----- >_______________________________________________ ----- >Sprinklerforum mailing list ----- >[email protected] ----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum ----- > ----- >To Unsubscribe, send an email ----- >to:[EMAIL PROTECTED] ----- >(Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)